The process by which heat energy in the form of light (usually IR unless the substrate is hot enough to glow in the visible range) is emitted more strongly by warm surfaces and absorbed by other materials especially those of low IR reflectivity (think matte black finish). Radiant heat transfer does not require a medium. Foam insulation materials, such as spray foam insulation, are opaque to thermal radiation, like most solid materials.

The problem was that the installer was doing his first spray foam job ever, and the thickness of the insulation varied from zero (visible roof deck) to about 9". Unfortunately, good average thickness doesn't cut it. The coverage needs to be uniform because a lot of heat will go through the under-insulated areas. (See my article on flat or lumpy insulation performance.)

One of the key differentiators between traditional insulation materials and spray foam insulation is the latter’s ability to insulate and air seal. Foam insulation provides an air barrier to wherever it is applied to help mitigate air leakage from the building. Air sealing the building envelope with sprayed-in foam insulation also helps address moisture ingress to reduce the risk of mold and mildew growth as well as the formation of ice dams in colder climate zones during the winter months.  When you compare foam insulation with traditional fiberglass insulation and cellulose insulation, sprayed insulation minimizes air infiltration, it assists in limiting moisture vapor from entering and escaping the home, which in turn reduces the load on heating and cooling systems. Below is a video that compares fiberglass, cellulose and open-cell spray foam in terms of insulating and air sealing value. https://youtube.com/watch?feature=player_embedded&v=ggLAUsiuI_o

Our commitment to using intelligent solutions and high-performing, quality products to help solve global environmental challenges is evident in both the use of renewable and recycled content in our products, as well as our green recognitions and certifications by various organizations, such as the NAHB Research Center, LEED Certifications, and USDA Bio-Preferred, just to name a few.
KARNAK manufactures a complete line of sustainable roof coatings, sealants, and waterproofing solutions certified to comply with UL, FM, CRRC, ENERGY STAR®, Dade County, Title 24, and Florida’s HVZ building code. Our ENERGY STAR-labeled coatings can help buildings obtain LEED points. With four factories and seven warehouses across the U.S., KARNAK’s dedicated sales and customer service team will deliver the products you need in less time than it takes our quick-dry 535 Envirolastic to cure.

Spray foam insulation or spray polyurethane foam (SPF) is an alternative to traditional building insulation such as fiberglass. A two-component mixture composed of isocyanate and polyol resin comes together at the tip of a gun, and forms an expanding foam that is sprayed onto roof tiles, concrete slabs, into wall cavities, or through holes drilled in into a cavity of a finished wall.

This website uses cookies and other tracking technologies (also known as pixels or beacons) to aid your experience (such as viewing videos), as well as “performance cookies” to analyze your use of this website and to assist with marketing efforts. If you click the "Accept All Cookies" button or continue navigating the website, you agree to having those first and third-party cookies set on your device. If you do not wish to accept cookies from this website, you can choose to not allow cookies from this website by updating your browser preferences. For more information on how we use Cookies, please read our Privacy Policy   Accept All Cookies

United Coatings™ Roof Coat Elastomeric Coating is an effective coating for providing long-term reflectivity over a wide range of roofing substrates. The high reflectivity of Roof Coat Elastomeric Coating keeps the roof substrate cool, which not only helps prolong its longevity but also helps save on energy costs. Roof Coat Elastomeric Coating’s rich consistency uniformly covers the textured profile of various substrates, forming a flexible monolithic membrane that provides protection from normal weathering, aging, and ultraviolet exposure.

I live in Baton Rouge LA with a very old and drafty house. There is no blockages in the walls between the crawl space and attic. Lots of critters just come on in. I would like to used closed cell sprayed under house to warm up floors and block moisture. I would like to spray closed cell into attic, but am afraid of enclosing attic due to moisture build-up. Can I spray closed cell against the attic floor in same way as installing bats, thus leaving my venting the same as it always has been. Other ideas? Thanks. https://www.youtube.com/embed/ggLAUsiuI_o
I have never used foam insulation before and this was easy for me to use right out of the box. I had a 4'x8"x8" cavity in my basement that houses a waterline. When the previous homeowner installed this they put no insulation in at all and being that it's an exterior wall in the basement and I live in the Midwest that thing was pushing so much cold air in it was incredibly uncomfortable. Out of the box and job completed in about 5 minutes. Stopped all drafts and created a nice 2" barrier on the wall in which I will install some extra bat insulation over it. 4 stars because the spray isn't very good passed 6-8" from the surface. Make sure you can reach the surface you want to coat. Great for small jobs! https://www.youtube.com/watch?v=ggLAUsiuI_o&app=desktop
Some states, municipalities and utilities have programs. Check with your coatings manufacturer for further information. As a membership benefit, RCMA provides maintains a database of current information on rebates and tax credits for installing reflective roofs. RCMA’s customized search tool can be used to find the most up-to-date listings of reflective roofing financial incentives available.
Yes, a new roof should be coated if the building owner wants to add a highly reflective roof coating to reduce energy costs. The buyer should be aware of any warranties provided for a new roof that may violate that warranty during the period it is in force via the use of a roof coating. This will extend the roof’s service life. A reflective roof coating will reduce the heat load on the roofing assembly.
Henry 587 Dura-Brite White Elastomeric Roof Coating is Henry 587 Dura-Brite White Elastomeric Roof Coating is a premium high solids formula offering better weather protection solar reflectivity and longevity than economy grade reflective roof coatings. Cured coating forms a permeable membrane which prevents liquid infiltration but allows moisture vapor to vent or breathe out of underlying substrate. Recommended ...  More + Product Details Close
Closed-cell spray insulation, a rigid medium-density material, can be used in exterior applications such as continuous insulation applications, as well as interior applications. This type of foam insulation has a higher R-value per inch making it also suitable for small areas that require the highest possible R-value to meet building code requirements. Closed-cell spray foam’s rigidity help reject bulk water making it a recognized flood-resistant material by FEMA.
Please Note: Prices, promotions, styles and availability may vary by store and online. Inventory is sold and received continuously throughout the day; therefore, the quantity shown may not be available when you get to the store. This inventory may include a store display unit. Online orders and products purchased in-store qualify for rebate redemption. Mail-in Rebate is in the form of merchandise credit check, valid in-store only. Merchandise credit check is not valid towards purchases made on MENARDS.COM®. By submitting this rebate form, you agree to resolve any disputes related to rebate redemption by binding arbitration and you waive any right to file or participate in a class action. Terms and conditions available at www.rebateinternational.com® 

There is a significant price difference when it comes to using foam insulation to insulate a new versus older home. Spraying insulation inside a newly constructed home is easier because the installation company can ensure the insulation will work effectively and design it for optimum defense against sound, heat transfer and utility costs. Installing spray foam in older homes that contain existing insulation can cost additional time and money -- it is not usually recommended as compared to weatherization or an energy aduit.
During colder months, 2 component foam is very sensitive to temperature variances. Per product instructions, both tank temperatures need to be above 70°F (21°C) for at least 24 hours prior to use. All application surfaces should be clean/dry and above 60°F (16°C) prior to application. Variance outside of the recommended temperature can affect foam yield and performance.

Roof coatings can add 25 years to the service life of a roof and reduce the amount of discarded roofing materials that end up in landfills. The infrared image on the right shows 175 °F (79 °C) on the uncoated (black) section of the modified bitumen roof. The coated (white) section is 79 °F (26 °C). Field studies have shown that cool roof coatings can lower rooftop temperatures and reduce air conditioning bills. http://y2u.be/ggLAUsiuI_o
Please Note: Prices, promotions, styles and availability may vary by store and online. Inventory is sold and received continuously throughout the day; therefore, the quantity shown may not be available when you get to the store. This inventory may include a store display unit. Online orders and products purchased in-store qualify for rebate redemption. Mail-in Rebate is in the form of merchandise credit check, valid in-store only. Merchandise credit check is not valid towards purchases made on MENARDS.COM®. By submitting this rebate form, you agree to resolve any disputes related to rebate redemption by binding arbitration and you waive any right to file or participate in a class action. Terms and conditions available at www.rebateinternational.com®
Air infiltration and exfiltration within a home contributes to almost 99% of moisture migration. Restricting air movement stops moisture accumulation so that the possibility of mold growth is less likely. Combined with a properly sized HVAC system, spray foam insulation helps control the indoor humidity levels to minimize moisture and condensation. Reducing moisture and controlling humidity can also add years to the life expectancy of a home, plus contribute to a healthier indoor environment. Finally, it also deters pests, making it difficult for them to nest.

Spray Foam Attic Insulation Cost


That’s $58.3 Billion dollars. That’s roughly how much money we wasted in 2010 in the US according to the Department of Energy because of air leaking out of our building envelopes. If your building leaks energy, you’re paying more for energy than you need to. Clearly you’re not alone. If you’re ready to claim your share of the savings, it’s quicker and easier than you think.
I am building a house in Central Texas (Caldwell). Several builders are cautious about using foam insulation and/or a closed attic. I would like to use both. Here in Texas, heat and humidity (except for the past few years of drought) are a continuing problem. Which type of foam would be the best to use in our home, where should the vapor barrier be or should be use one at all, if we are using fans in the exterior walls to supply fresh air to the house, do we need a vented attic or will it cause more problems than it solve? I have printed out your article and the blogs to give to my contractors and architect, but I would really appreciate your comments on the products being used in my part of the US.  

Typical roof coating dry film thickness vary from paint film thickness (plus or minus 3 dry mils) to more than 40 dry mils. This means a roof coating actually becomes the top layer of a composite roof membrane and underlying system. As such, the roof coating is the topmost layer of protection for the membrane, receiving the impact of sunlight (both infrared and ultraviolet (UV), rain, hail and physical damage.
once the foam is installed correctly, it is a inert plastic not much different than the foam cushions you sit on. there is not a health rick unless you have off ratio uncured foam that has not mixed properly. the foam is absolutely a health risk in its raw forms before it is mixed and cured. You should not be in the building without proper respirators and eye protection. The spray foam industry should be controlled and regulated by the same standards, testing and inspections that framing ,electrical and plumbing are. until that happens then you will have idiots with spray rigs ruining peoples homes and ruining the market for honest foam contractors that know how to price a job fairly and complete it correctly.
Installing spray foam is easy to do and can dramatically improve a building or home’s energy efficiency and thermal resistance. Our closed cell foam is so efficient just 3 inches of foam appled inside of wall cavities provides an insulation value of over R18!. Our products are specially formulated for both new construction and existing homes and buildings. 

Sta-Kool 780 Siliconized Acrylic White Elastomeric Roof Coating Sta-Kool 780 Siliconized Acrylic White Elastomeric Roof Coating is a high quality flexible white acrylic roof coating. Product is enhanced with silicone for improved water resistance adhesion and life expectancy. Product resists cracking peeling while offering tremendous durability and long term life. The coating forms a durable protective barrier which ...  More + Product Details Close

I live in Baton Rouge LA with a very old and drafty house. There is no blockages in the walls between the crawl space and attic. Lots of critters just come on in. I would like to used closed cell sprayed under house to warm up floors and block moisture. I would like to spray closed cell into attic, but am afraid of enclosing attic due to moisture build-up. Can I spray closed cell against the attic floor in same way as installing bats, thus leaving my venting the same as it always has been. Other ideas? Thanks.

Spray Foam Professionals


Installing spray foam is easy to do and can dramatically improve a building or home’s energy efficiency and thermal resistance. Our closed cell foam is so efficient just 3 inches of foam appled inside of wall cavities provides an insulation value of over R18!. Our products are specially formulated for both new construction and existing homes and buildings.


Low-density foam is applied as low or high-pressure, two-component polyurethane spray foam. Low-density spray foam can be applied on walls, in unvented attics, to ducts and ceilings, and in vented attics and crawl spaces. It is known as an air barrier, but permeable to vapor and moisture. It is often used to fill cavities in walls during construction.
This high R-value of 4.45 at 1 inch, polyurethane insulation expands to seal cracks, gaps, and voids in attics, walls, crawl spaces, and ceilings. Agribalance is a three-quarter pound density foam that reduces air leakage by improving energy efficiency, and reducing moisture intrusion and outside contaminants such as dust, dirt, and allergens. As a result, builders can generally install smaller, more energy-efficient HVAC systems and achieve similar, or superior comfort compared to traditionally insulated structures which require a larger, less efficient HVAC system – resulting in higher energy costs.

Spray Foam Insulation Cost


However, coating asphalt shingles and built-up composition roofs requires more caution. The National Roofing Contractors Association’s (NRCA) director of technical services has stated "The roofing industry is aware of a number of issues that could have negative consequences for field application of coatings over asphalt shingle roof systems. Anyone considering this type of application should be aware of the concerns so they can weigh them against the benefits claimed in coating product promotional materials."[2]
Sean, thanks for jumping in and answering John's questions. About choosing the right foam, I intentionally avoided the open cell vs. closed cell foam debate. I did this partly because it's worthy of an article all by itself, but mainly I didn't include it because, despite all the warnings the two sides issue about the other, I've never personally seen a problem caused by using open cell where they should've used closed cell or vice versa. I'm sure things like that happen; I just haven't seen it yet.
We are turning our roof into an unvented roof assembly by raising the roof and blowing in SPF. We are planning to leave the existing vapor barrier down but remove the fiberglass batting and then adding 6" of SPF in all the cavities, to completely seal and insulate the house. Should we have any concerns about doing it "upside down" and not spraying the foam directly to the underside/sheathing of the roof?

This high R-value of 4.45 at 1 inch, polyurethane insulation expands to seal cracks, gaps, and voids in attics, walls, crawl spaces, and ceilings. Agribalance is a three-quarter pound density foam that reduces air leakage by improving energy efficiency, and reducing moisture intrusion and outside contaminants such as dust, dirt, and allergens. As a result, builders can generally install smaller, more energy-efficient HVAC systems and achieve similar, or superior comfort compared to traditionally insulated structures which require a larger, less efficient HVAC system – resulting in higher energy costs.

Spray Foam Insulation Cost


Open-cell is also known as half-pound foam. It has an R-Value of 3.5-3.6 per inch, and its density is bout 0.5 pounds per cubic food. Low-density foams like these are made partially from raw biological materials Carbon dioxide or water is also used in the makeup. Open-cell uses far less material than closed-cell, but its R-Value is lower. Also, open cell requires a vapor retarder (like gypsum wallboard) and is riskier when used for roof sheathing. It's not highly recommended that you use open-cell insulation if you live in a cold climate unless you have that extra barrier. You should also compare how much money you spend versus how effective the open-cell insulation is wherever it's installed.
Sealection 500 is a cutting-edge formula of open-cell spray foam insulation, which expands 120 times its liquid volume to insulate and seal all cracks, gaps, and joints with a single application, and is easy to install and finish. It has dramatically increased energy efficiency for millions of residential and commercial property owners. This translates to a high-performing product for builders, shorter application, and finishing times for contractors, and lower energy bills for homeowners and commercial building owners. http://www.youtube.com/watch?feature=player_embedded&v=ggLAUsiuI_o
United Coatings™ Roof Coat Elastomeric Coating is an effective coating for providing long-term reflectivity over a wide range of roofing substrates. The high reflectivity of Roof Coat Elastomeric Coating keeps the roof substrate cool, which not only helps prolong its longevity but also helps save on energy costs. Roof Coat Elastomeric Coating’s rich consistency uniformly covers the textured profile of various substrates, forming a flexible monolithic membrane that provides protection from normal weathering, aging, and ultraviolet exposure.
I used this for the rim-joist in our home. A couple things: I put 1in solid core foam (cut to size) in each bay before using the spray foam. I also was able to do a relatively 'thick' spray to close off any potential gaps that may have existed. I turned off the HVAC and turned on some fans in the windows to exhaust out the fumes, and wore a mask (3m respirator).
Light-density open-cell SPF is commonly known as half-pound foam. It is a semi-rigid material with a sponge-like appearance that expands during installation and creates small, open cells that are filled with carbon dioxide. Due to its ability to expand during the application process, it fills cracks, crevices and voids and adheres to irregular surfaces or substrates to form an air sealing insulation.[12]
If you don't have the patience to slowly fill the void with spray foam through holes drilled in one of the studs, you could (if you were an experienced carpenter) use a Sawzall to remove one of the studs and re-frame the corner as a two-stud corner. Then you could either insulate the void with a fiberglass batt or simply present the two-stud corner to the spray-foam contractor as an accessible corner.

In general, cantilevered steel beams are a nightmare. If part of the steel beam is in contact with exterior temperatures, then it's best if the interior portion of the steel beam is covered on all sides with insulation. This is generally impossible (because the interior portion of the cantilevered beam generally supports a load, meaning that you can't wrap the steel beam in insulation on all sides).
DID YOU KNOW? Spray FOam insulation out-performs conventional insulation materials because they (conventional insulation materials) trap still-dry air and if that air moves or becomes wet, the thermal resistance can drop by 50%. Spray Foam protects against air infiltration, which can increase energy costs in buildings by 10 to 40%. Eliminate these drafts and live in a more energy-efficient, comfortable and healthier building by choosing spray foam insulation.
Although spray polyurethane foam has many advantages over other types of insulation, spray foam installation isn’t foolproof. Some builders have reported problems with sloppy foam insulation. For example, some installers have been known to begin spraying before the chemical components are up to temperature, which can affect component mixing and foam performance. When components are poorly mixed, or mixed in the wrong ratio or at the wrong temperature, cured foam has been known to shrink away from rafters or studs, leaving cracks. Some installers rush through their spraying, resulting in voids.
Prices, promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.
R-value is the term given to thermal resistance to heat flow. The higher the R-value of an insulation product, the more effective the insulation properties. Spray polyurethane foam comes in a range of densities and cel structure. Low density foams are referred to as Open Cel SPF while higher density foams are referred to as Closed Cel foam. 1.8-2 pound polyurethane foam has the highest R-value of readily available spray foam insulation used in homes and buildings.[4]
I'm in the process of redoing my basement and read through the posts. I took out one inch styrofoam covered by 1/4 " beadboard and installed 2X4s and plan on putting in fiberglass batts between them(r-13) with 1/2 in drywall over top of that. Do you think I will see a significat increase in heat control? Should I have done more?... it's a little after the fact, but still curious to know if I will see a big difference based on your experience.
Spray foam insulation works by sealing the building envelope to stop conditioned air from escaping and prevent unwanted outside air from entering your home. It allows efficient use of your HVAC system and helps regulate the temperature fluctuations and humidity in your home. It's a lightweight, durable, and versatile insulation solution boasting the industry’s strongest performance in energy efficiency and energy cost savings. http://youtube.com/e/ggLAUsiuI_o?app=desktop
Starting a new build (1 1/2 basement walkout), all 2x6 exterior walls w/ brick veneer in CZ3. Above grade, would like to do spray foam in 2x6 walls, 1/2" or 1" of rigid foam board on the exterior, and a 1" air gap. Will this require a house wrap or can I do w/o the rigid foam and go with a housewrap? Also, any recommendations about insulation strategies for the finished basement. Thanks! http://youtube.com/e/ggLAUsiuI_o
If you cut the nails holding one of the corner studs to the bottom plate and the top plate with a Sawzall, you can use a flat bar (or a flat bar plus a wrecking bar) to pull the stud off the sheathing nails. Either re-use the stud, or buy a new stud, and install the stud with toenails as shown in the link I provided in Comment #51 (this link: Outside corner detail). http://m.youtu.be/ggLAUsiuI_o
Elastomeric coatings offer effective and affordable solutions for fixing roof leaks. The coatings can be used to repair any type of roof leak. The elastomeric roof coatings can be used throughout the year because they stretch and contract easily to adjust to winter and summer temperatures. It is usually made using polymeric products such as acrylic alongside white pigments like titanium dioxide. This helps create an opaque and reflexive final product.
The process by which heat energy in the form of light (usually IR unless the substrate is hot enough to glow in the visible range) is emitted more strongly by warm surfaces and absorbed by other materials especially those of low IR reflectivity (think matte black finish). Radiant heat transfer does not require a medium. Foam insulation materials, such as spray foam insulation, are opaque to thermal radiation, like most solid materials.
If you cut the nails holding one of the corner studs to the bottom plate and the top plate with a Sawzall, you can use a flat bar (or a flat bar plus a wrecking bar) to pull the stud off the sheathing nails. Either re-use the stud, or buy a new stud, and install the stud with toenails as shown in the link I provided in Comment #51 (this link: Outside corner detail). http://m.youtu.be/ggLAUsiuI_o
Spray foam insulation, when properly installed is both an air barrier and when closed cell foam is used at the proper depth a vapor barrier!  Before hiring any contractor you should establish the brand of foam being used and verify that with the named manufacture.  Please ask for ESR reports and MSDS sheets on any foam being installed in your home. A couple areas where you might consider spray foam insulation include: http://www.youtube.com/v/ggLAUsiuI_o&feature=share

In general, cantilevered steel beams are a nightmare. If part of the steel beam is in contact with exterior temperatures, then it's best if the interior portion of the steel beam is covered on all sides with insulation. This is generally impossible (because the interior portion of the cantilevered beam generally supports a load, meaning that you can't wrap the steel beam in insulation on all sides). https://m.youtu.be/ggLAUsiuI_o

Both high and low-pressure, two-component spray foam are applied by professional contractors who are trained to use and apply SPF with the required equipment (protective gear, full eye protection, respirators, and gloves). Contractors should follow the ventilation recommendations by the product manufacturer to avoid overexposure through inhalation, and instruct those without protective gear (homeowners or building occupants) to stay away from the work area during exposure times and to not return until instructed by the professional contractor.


Excellent kit for insulating a house. Slow rising foam takes longer to insulate an area as you must do it in layers 1" thick. Any thicker can overheat the chemicals and prevent a proper cure and off-gassing. Recommend purchasing a second suit and nozzles so you can use it multiple days to achieve the thickness desired for the highest R value. Seals up and insulates much better than traditional fiberglass. The sound suppression is noticeably different. Used it to insulate the ceiling above our bedroom. The sound is remarkably more quiet than the fiberglass insulation we had before. The only down side is the weight of the containers. Using a smaller kit would be easier to handle and move around when spraying a ceiling in an attic. A word of caution, use plywood that spans at least 2 joist per container when spraying in an attic to hold the weight.
Find spray foam contractors, suppliers, equipment, news, and technical information about spray foam insulation, foam roofing, and protective coatings. If you are a homeowner, builder/architect, or interested to get into the spray foam business, we have set-up special areas just for you. Check out our information packed Spray Foam Guides to learn more.
Spray foam is a fully adhered insulation that is spray applied into wall cavities, providing a continuous air and moisture barrier. Spray foam allows efficient use of your HVAC system and helps regulate the temperature fluctuations and humidity in your home. Spray foam effectively seals the building envelope, filling in any cracks and crevices, the common source of air and moisture infiltration as well as temperature variations. https://www.youtube.com/v/ggLAUsiuI_o&feature=youtu.be
Spray polyurethane foam, or SPF, is the main type of 2-part, closed-cell spray foam used by insulation contractors. Large-scale insulation jobs require special equipment as well as safety gear to protect the installer from chemical fumes during installation. When the foam cures and hardens just several minutes after application, it's completely safe for as long as it stays in place.
To avoid the expense re-roofing a house that is simply suffering from nail fatigue, and to obtain optimum insulation, an 85mm layer of polyurethane foam can be sprayed onto the underside of the slates or tiles of a pitched roof. This stabilises and weatherproofs the roof by fixing the nails, battens and roofing felt. As the foam is a superior insulant, coupled with just 100mm of insulation at joist level, your roof will also meet the stringent thermal performance standards required for a new home. A typical roof can be insulated using the polyurethane treatment for around half the cost of re-roofing.
Spray foam is a chemical product created by two materials, isocyanate and polyol resin, which react when mixed with each other and expand up to 30-60 times its liquid volume after it is sprayed in place. This expansion makes it useful as a specialty packing material which forms to the shape of the product being packaged and produces a high thermal insulating value with virtually no air infiltration.
As this example illustrates, it's important to seal the envelope completely. One of spray foam's biggest selling points is its air-sealing ability, but it can't seal places where it's not sprayed. One of the nice things about using spray foam in new construction is that you can do a Blower Door test before the drywall goes in. Even better, you can test for leaks with a fog machine.
Our commitment to using intelligent solutions and high-performing, quality products to help solve global environmental challenges is evident in both the use of renewable and recycled content in our products, as well as our green recognitions and certifications by various organizations, such as the NAHB Research Center, LEED Certifications, and USDA Bio-Preferred, just to name a few.

Whether you’re sending something fragile in the mail or keeping valuables safe during a move, secure packing is everything. To protect a delicate item, simply fill a spare shopping bag half-full with spray insulation foam and place in the bottom of a box, pressing the item gently into the bag as it hardens to cushion the item. Repeat for the top and you have a DIY custom packaging solution that can handle the rigors of delivery.

I used this product to seal and insulate my rim joists as I am finishing the basement. The builder used R13 batt insulation when we built the house 3 years ago. I use a dehumidifier to control moisture in the basement which is below grade. The setting I use is 55%. The dehumidifier kicks on periodically and requires emptying every few days. Since using the foam all around the house on the rim joists and sill plate, the dehumidifier has stayed at 50% for over two weeks since spraying and rarely turns on anymore. I also put the original R13 batt insulation back up after the foam cured.

How Much For Spray Foam Insulation

×