I live in Baton Rouge LA with a very old and drafty house. There is no blockages in the walls between the crawl space and attic. Lots of critters just come on in. I would like to used closed cell sprayed under house to warm up floors and block moisture. I would like to spray closed cell into attic, but am afraid of enclosing attic due to moisture build-up. Can I spray closed cell against the attic floor in same way as installing bats, thus leaving my venting the same as it always has been. Other ideas? Thanks.
SPF insulation applied by professionals is usually described as either a high- or low-pressure foam and is available as either open- or closed-cell. Each type has advantages and disadvantages depending on the application requirements. The comparison chart below can be helpful in explaining or understanding which type of SPF insulation is best suited to a specific application.
During colder months, 2 component foam is very sensitive to temperature variances. Per product instructions, both tank temperatures need to be above 70°F (21°C) for at least 24 hours prior to use. All application surfaces should be clean/dry and above 60°F (16°C) prior to application. Variance outside of the recommended temperature can affect foam yield and performance.
Starting a new build (1 1/2 basement walkout), all 2x6 exterior walls w/ brick veneer in CZ3. Above grade, would like to do spray foam in 2x6 walls, 1/2" or 1" of rigid foam board on the exterior, and a 1" air gap. Will this require a house wrap or can I do w/o the rigid foam and go with a housewrap? Also, any recommendations about insulation strategies for the finished basement. Thanks!
I started watching back in the Bob Villa days. It's funny when Bob left the show I thought well that's the end of my favorite show. I couldn't have been more wrong. TOH has gotten better and better over the years. I've gotten so many great ideas for my houses from watching close to every episode of TOH. Also, my confidence in being able to take on more and more complex projects at home has grown thanks to Norm, Tommy and Roger. Sorry Richard, I love watching you and learning about the latest greatest plumbing, heating and cooling tech but I hate doing plumbing stuff. My favorite projects would be #1 Carlisle House in 2004 and #2 Cambridge House in 2005. I've watched those seasons multiple times since becoming an Insider. Kevin is by far my favorite TOH host. His first couple of seasons were rough but once he hit his stride he just got better and better. I absolutely love it when Kevin and Tommy do their 'Sonny and Pops' routine. Who wouldn't want Tommy Silva to be their Pops! Thank you for 40 great years!
Note: The practice of foam insulating the attic has raised eyebrows in the building industry because "standard" roofing techniques call for the attic to be ventilated; however, in a vented attic situation it will become approximately 130 degrees in the summer. There's no reason for an air-conditioning and vent-ductwork to have to work in that type of severe conditions. By applying Icynene right on the underside of the roof deck, the severe temperatures no longer exist in the attic. In short, the attic is now a "conditioned" space of the house that is just as comfortable as any other room in the home. This is called a "Compact Roof", which means you can frame right up against it. The one drawback of using expanded foam on the inside of the roof is that this will cause the temperature of the shingles to rise, but how much is not yet known. And how much damage a rise in temperatures could cause is debatable.

How Much Is Attic Spray Foam


If you haven’t considered spray foam insulation, now may be the time to start looking into it. As you know, having proper insulation will help reduce your heat and air conditioning bills. In specific, spray foam insulation can be particularly helpful during renovations. It can provide a barrier between outside walls, and even a sound barrier for the inside.


In general, cantilevered steel beams are a nightmare. If part of the steel beam is in contact with exterior temperatures, then it's best if the interior portion of the steel beam is covered on all sides with insulation. This is generally impossible (because the interior portion of the cantilevered beam generally supports a load, meaning that you can't wrap the steel beam in insulation on all sides).
Q. "I talked to a building product supplier for WALLTITE spray foam, he is suggesting to use 2" or 3" of closed cell-spray foam in the joists areas instead of the batts insulation. He says it will work with outboard rigid insulation. There is a location of a cantilevered floor area with steel beam so I may need to use spray foam to protect the steel beam. It would then be convenient continue to spray in the floor joist cavities and then apply 5" of polyiso outboard of the bottom cantilever floor sheathing."
Roof coatings are easy to install. Smaller roofs in good, serviceable condition can be a weekend do-it-yourself (DIY) project. Larger roofs with leaks and ponding water issues should be coated by a qualified professional. Additional roof coating products, such as foam or coatings designed for seams, may be required underneath the main coating layers. Supplement coating products are used to reinforce damaged or leak-prone problem areas.[3] http://www.youtube.com/v/ggLAUsiuI_o&feature=youtube_gdata
Sporadic cases of hypersensitivity pneumonitis (HP) have also been reported in workers exposed to isocyanates. The symptoms may seem like the flu, with fever, muscle aches, and headaches. Other symptoms may include a dry cough, chest tightness, and difficult breathing. Individuals with chronic HP often experience progressively more difficult breathing, fatigue, and weight loss. Individuals with acute HP typically develop symptoms 4–6 hours after exposure.[4]
If you’re not familiar, spray foam is a type of insulation that expands after you spray. The foam expands and seals, avoiding any type of unnecessary moisture (which can create mold) or encouraging pests to eat through your walls. It protects the lining of your house, and even can protect the heating and cooling of your house during those unbearably cold or hot days. http://m.youtube.com/watch?feature=player_embedded&v=ggLAUsiuI_o
I don't even want to ask this question but... several years ago we hired a local contractor to spray high density foam on the roof deck and walls of our unfinished 2nd floor. We realized that the job was done poorly and cut an access into the attic space to assess things. We realize now that they spray foamed directly to the chimney (no flashing). The chimney is currently used for a woodstove and DHW venting. The DHW will go away but wood stove will remain. My question is, how bad (unsafe) is this? I have found information on foam exposure to fire but have not been able to find anything about temperature ratings in general (i.e. what happens on prolonged exposure to high temperatures).
Loctite tite foam is a new generation of Loctite tite foam is a new generation of polyurethane-based insulating foam sealant that expands to fill seal and insulate gaps and cracks inside or out. It is white polymer foam based on purified and concentrated ingredients that provides 4 times more density versus conventional foams for better durability and insulation. ...  More + Product Details Close

Here's a simpler, less expensive alternative: Cut some 2-inch-thick rigid-foam insulation and glue it to the subfloor between the joists or support it with nails driven partway into the joists. Then fill any gaps between the edges of the foam boards and the joists using the canned spray foam sold at home centers or hardware stores. An even easier option is to nail the foam panels against the bottom edge of the joists and seal the joints with canned foam, but you'll lose some headroom and access to any pipes and wires between the joists. As with spray-foam kits, protect yourself and the floor from the dripping globs of canned foam. A full face shield, gloves, and a hat would be a good start.
Light-density open-cell SPF is commonly known as half-pound foam. It is a semi-rigid material with a sponge-like appearance that expands during installation and creates small, open cells that are filled with carbon dioxide. Due to its ability to expand during the application process, it fills cracks, crevices and voids and adheres to irregular surfaces or substrates to form an air sealing insulation.[12]
I live in Baton Rouge LA with a very old and drafty house. There is no blockages in the walls between the crawl space and attic. Lots of critters just come on in. I would like to used closed cell sprayed under house to warm up floors and block moisture. I would like to spray closed cell into attic, but am afraid of enclosing attic due to moisture build-up. Can I spray closed cell against the attic floor in same way as installing bats, thus leaving my venting the same as it always has been. Other ideas? Thanks.

Spray Foam Professionals


Henry 287 Solar-Flex White Roof Coating is a Henry 287 Solar-Flex White Roof Coating is a premium elastomeric water-based acrylic latex coating designed to reflect the sun's heat and UV rays. Properly applied it is highly resistant to disbonding chalking mildew and discoloration. Expands and contracts with your roof to protect it from leaks aging mold mildew and ...  More + Product Details Close
Light-density open-cell SPF is commonly known as half-pound foam. It is a semi-rigid material with a sponge-like appearance that expands during installation and creates small, open cells that are filled with carbon dioxide. Due to its ability to expand during the application process, it fills cracks, crevices and voids and adheres to irregular surfaces or substrates to form an air sealing insulation.[12]
What do you mean by "our AC units require fresh air ventilation"? Fresh air doesn't come from the attic. If there's an atmospheric combustion appliance in the attic, such as an 80 AFUE furnace, then you shouldn't be encapsulating the attic anyway. If that's the case, you don't want spray foam on the roofline at all. You can either change out the furnace to a sealed combustion unit or do your insulating and air-sealing at the flat-ceiling level.

Loctite tite foam is a new generation of Loctite tite foam is a new generation of polyurethane-based insulating foam sealant that expands to fill seal and insulate gaps and cracks inside or out. It is white polymer foam based on purified and concentrated ingredients that provides 4 times more density versus conventional foams for better durability and insulation. ...  More + Product Details Close
Roof Coatings should not be confused with deck coatings. Deck coatings are traffic bearing - designed for waterproofing areas where pedestrian (and in some cases vehicular) traffic is expected. Roof coatings will only waterproof the substrates but will not withstand any kind of on going use by people or vehicles (such as walkways, patios, sundecks, restaurants, etc.).
The average price to cover 200 square feet with a foam insulation kit will run between $300 and $600 (about two to three kits). Inside these kits is something called Icynene, a foam made from two liquids that are heated and pushed through a gun on the can. When Icynene is released, it expands up to 100 times its size as it hits the surface area you're covering. These can contain a lot of gasses, making its installation a dangerous process. Even low-pressure sprayers can be harmful to homeowners' health.
If you haven’t considered spray foam insulation, now may be the time to start looking into it. As you know, having proper insulation will help reduce your heat and air conditioning bills. In specific, spray foam insulation can be particularly helpful during renovations. It can provide a barrier between outside walls, and even a sound barrier for the inside.
If you’re not familiar, spray foam is a type of insulation that expands after you spray. The foam expands and seals, avoiding any type of unnecessary moisture (which can create mold) or encouraging pests to eat through your walls. It protects the lining of your house, and even can protect the heating and cooling of your house during those unbearably cold or hot days.
When it comes to insulating the house, fiberglass tends to be the common form of insulation. However, after comparing fiberglass and spray foam insulation, it’s shocking how fiberglass tends to be the lesser of the two. Although it has deemed reliable over the years, there are way more benefits to insulating your home with spray foam. One of those benefits includes regulating the temperature of your house.
Sealection® 500 has been Demilec's flagship product for more than 20 years, and has positioned Demilec as an industry-leading spray foam insulation manufacturer. As an environmentally-friendly product, it delivers superior performance, energy savings, and is an excellent return on investment for architects, builders, contractors, and homeowners, making it the ideal choice for insulation.
This is more common with closed cell foam, but it happens with open cell foam, too. Since closed cell foam has a higher R-value per inch, installers generally spray 2" in walls and 3" in rooflines to meet the energy code requirements of R-13 and R-19, respectively. (I'm not going to dive into the energy code here, but these numbers apply to many climate zones, the latter being allowed under the UA tradeoffs rule. See the Energy Nerd's blog on this topic if you want to argue.)

We live in middle TN and had our house foamed last year. We noticed recently that some of the foam was shrinking and seperating from the floor joists. We contacted the installer and he informed us that the manufacturer had a problem with a batch of foam during the time frame we had our house sprayed. The contractor wasn't sure if we had the recalled batch installed in our house or not. He said he would check the batch numbers and let us know. He seems like a nice guy promising to do whatever it takes to fix any problems. Do we trust him, however, to be truthful about the batch number? Do we have any options for finding out the information ourselves? I inspected the entire crawl space of the house and noticed approximately (5) areas that were seperating and a couple areas where the foam didn't adhere to the block. Do I assume by it being so infrequent that it is nothing to be concerned about? My concern is the walls that are not capable of being visually inspected because of sheetrock.


There are several types of reflective roof coatings that impart varied reflectance rates/ values. Typically, the reflective coatings are what are commonly referred to as white coatings and there are also aluminum coatings typically used with asphalt. Highly reflective white roof coatings are typically comprised of acrylics, urethanes, silicones, SBS, SEBS, and other types. https://www.youtube.com/watch?v=ggLAUsiuI_o&app=m

There are several types of reflective roof coatings that impart varied reflectance rates/ values. Typically, the reflective coatings are what are commonly referred to as white coatings and there are also aluminum coatings typically used with asphalt. Highly reflective white roof coatings are typically comprised of acrylics, urethanes, silicones, SBS, SEBS, and other types. https://www.youtube.com/watch?v=ggLAUsiuI_o&app=m
Open-cell is also known as half-pound foam. It has an R-Value of 3.5-3.6 per inch, and its density is bout 0.5 pounds per cubic food. Low-density foams like these are made partially from raw biological materials Carbon dioxide or water is also used in the makeup. Open-cell uses far less material than closed-cell, but its R-Value is lower. Also, open cell requires a vapor retarder (like gypsum wallboard) and is riskier when used for roof sheathing. It's not highly recommended that you use open-cell insulation if you live in a cold climate unless you have that extra barrier. You should also compare how much money you spend versus how effective the open-cell insulation is wherever it's installed.

How Much To Charge For Spray Foam Insulation


Elastomeric coatings offer effective and affordable solutions for fixing roof leaks. The coatings can be used to repair any type of roof leak. The elastomeric roof coatings can be used throughout the year because they stretch and contract easily to adjust to winter and summer temperatures. It is usually made using polymeric products such as acrylic alongside white pigments like titanium dioxide. This helps create an opaque and reflexive final product.
Simple – we’ve seen experienced contractors work with the separate nitrogen tanks and spray foam rigs and have one heck of a time. These spray foam insulation kits are quick to learn and simple to use. They’re designed to be easy so you get results the very first time you spray. Thorough Instructions, 24/7 Product Support, and videos make it easy to install.
We are turning our roof into an unvented roof assembly by raising the roof and blowing in SPF. We are planning to leave the existing vapor barrier down but remove the fiberglass batting and then adding 6" of SPF in all the cavities, to completely seal and insulate the house. Should we have any concerns about doing it "upside down" and not spraying the foam directly to the underside/sheathing of the roof?
Foam is very sticky; you'll need to wear disposable coveralls with a hood, and gloves, a face mask, and eye protection. It takes some practice to spray foam evenly and, because it expands so dramatically, to control its depth; 2 inches is all you need to seal the joist cavities. You need a clear area so that you can work without interruption; any pause longer than 30 seconds will clog the nozzle and require putting on a new one. It's also critical that the air temperature stays between 75 and 85 degrees.
For maximum durability and leak resistance, we recommend that two coats of topcoat be applied at 100 sq. ft. per gallon, or a minimum of 20 mils dry coating. If two complete topcoats are not applied, always apply two thick coats to problem areas such as scuppers, drain areas, ponding areas, seams, and repaired areas. Avoid using Elastek Solar Magic™ or The Shield™ on ponding roofs. Clean skin and tools promptly with water.
Acrylic coatings are typically applied in two coats, with the second running perpendicular to the first. 1 gallon per 100 square feet is a good estimate for these coatings, as they do not need to be applied nearly as thick as many other coatings. These coatings can be sprayed or roll-applied. Acrylic coatings generally require a re-coat within 2-3 years of application.

If you haven’t considered spray foam insulation, now may be the time to start looking into it. As you know, having proper insulation will help reduce your heat and air conditioning bills. In specific, spray foam insulation can be particularly helpful during renovations. It can provide a barrier between outside walls, and even a sound barrier for the inside.
Air infiltration and exfiltration within a home contributes to almost 99% of moisture migration. Restricting air movement stops moisture accumulation so that the possibility of mold growth is less likely. Combined with a properly sized HVAC system, spray foam insulation helps control the indoor humidity levels to minimize moisture and condensation. Reducing moisture and controlling humidity can also add years to the life expectancy of a home, plus contribute to a healthier indoor environment. Finally, it also deters pests, making it difficult for them to nest. http://youtu.be/ggLAUsiuI_o

Spray foam is a fully adhered insulation that is spray applied into wall cavities, providing a continuous air and moisture barrier. Spray foam allows efficient use of your HVAC system and helps regulate the temperature fluctuations and humidity in your home. Spray foam effectively seals the building envelope, filling in any cracks and crevices, the common source of air and moisture infiltration as well as temperature variations.
While coatings may potentially stop minor leaks, the roof should be properly repaired and dried prior to coating application. Coatings may be able to seal pinhole leaks, which are leaks not visible to the naked eye. If the roof is leaking, the roof leak will need to be identified and repaired prior to any recoating; do not expect the coating to find and seal the leaks.
Light-density open-cell SPF is commonly known as half-pound foam. It is a semi-rigid material with a sponge-like appearance that expands during installation and creates small, open cells that are filled with carbon dioxide. Due to its ability to expand during the application process, it fills cracks, crevices and voids and adheres to irregular surfaces or substrates to form an air sealing insulation.[12] https://www.youtube.com/watch?v=ggLAUsiuI_o&feature=kp
Although spray polyurethane foam has many advantages over other types of insulation, spray foam installation isn’t foolproof. Some builders have reported problems with sloppy foam insulation. For example, some installers have been known to begin spraying before the chemical components are up to temperature, which can affect component mixing and foam performance. When components are poorly mixed, or mixed in the wrong ratio or at the wrong temperature, cured foam has been known to shrink away from rafters or studs, leaving cracks. Some installers rush through their spraying, resulting in voids.

If you haven’t considered spray foam insulation, now may be the time to start looking into it. As you know, having proper insulation will help reduce your heat and air conditioning bills. In specific, spray foam insulation can be particularly helpful during renovations. It can provide a barrier between outside walls, and even a sound barrier for the inside.

I have never used foam insulation before and this was easy for me to use right out of the box. I had a 4'x8"x8" cavity in my basement that houses a waterline. When the previous homeowner installed this they put no insulation in at all and being that it's an exterior wall in the basement and I live in the Midwest that thing was pushing so much cold air in it was incredibly uncomfortable. Out of the box and job completed in about 5 minutes. Stopped all drafts and created a nice 2" barrier on the wall in which I will install some extra bat insulation over it. 4 stars because the spray isn't very good passed 6-8" from the surface. Make sure you can reach the surface you want to coat. Great for small jobs!
I'm in the process of redoing my basement and read through the posts. I took out one inch styrofoam covered by 1/4 " beadboard and installed 2X4s and plan on putting in fiberglass batts between them(r-13) with 1/2 in drywall over top of that. Do you think I will see a significat increase in heat control? Should I have done more?... it's a little after the fact, but still curious to know if I will see a big difference based on your experience.
We are your allies in the victory over energy loss. Our mission is to educate our clients and community on the rewards of energy efficiency using a combination or the straight forward Sprayfoam insulation solution. By evaluating the needs of the development planned structures, budgets involved, and goals of the builder or individual homeowners, we compose a comprehensive work scope designed to tighten the thermal envelope and improve indoor air quality and acoustics, all while lowering operating costs and still creating homes that breathe. With over 50 years of combined experience and pages of 'Home Energy Reports' with 98% energy loss numbers — we help you begin your journey of offering homes energy independence and extreme comfort.   https://m.youtube.com/e/ggLAUsiuI_o
The guys who sprayed my attic were trained and certified, but I later found out, too late, that they had no experience and my attic was the first they'd ever sprayed. I was also never told to vacate my house for any length of time, and so I (and my pets) were in the house the day they sprayed and the entire time the off ratio foam was filling my home with horrendous vapors. The company kept telling me that it was a good job and I had nothing to worry about, even after I'd had 2 other experienced sprayers from 2 different companies visually examine the foam and confirm that large areas appeared to be off ratio. The 3rd sprayer from yet another company, was also outraged because the company who did my attic had failed to vacuum up all of the old cellulose insulation, and he also noticed areas where the foam was shrinking or pulling away, and this was not even 5 weeks after the spraying.  
Today’s “third generation” of blowing agents have a GWP of 700 to 1000 which is still remarkably high considering water/CO2 has a GWP of 1. However, innovation from some chemical manufacturers like the Chemours Company have introduced the next generation of HFO blowing agents such as Opteon 1100, which significantly reduces the GWP impact when using closed-cell spray foam insulation products.

Spray Foam Walls


Builders often turn to high-density SPF when high insulation values and strength are needed. As its name implies, this foam has a denser structure than either of the other SPF types. Therefore, it does not expand as much as lower density foams and requires more material to cover and insulate any given space. This spray foam is often an excellent choice for roofing or other exterior insulation because of its seamless, monolithic nature. High-density SPF can also help reduce energy costs significantly over a roof’s lifetime due to its thermal resistance properties. It also offers increased protection against air and water infiltration and strengthens the structure to which it is applied. The bond that SPF forms to the roof can increase a building’s resistance to wind uplift, which can help reduce damage experienced during periods of high wind.
Some states, municipalities and utilities have programs. Check with your coatings manufacturer for further information. As a membership benefit, RCMA provides maintains a database of current information on rebates and tax credits for installing reflective roofs. RCMA’s customized search tool can be used to find the most up-to-date listings of reflective roofing financial incentives available.
You've got no argument from me there, Dennis. Getting a good installer if you're going with spray foam is crucial. Many builders or homeowners don't know how to find one, however, and that's where third party inspections come in. Also, even good installers have bad days, but if someone comes in behind them with a measuring probe and a Blower Door, there will be fewer sub-par foam jobs.   https://www.youtube.com/v/ggLAUsiuI_o?version=3
To avoid the expense re-roofing a house that is simply suffering from nail fatigue, and to obtain optimum insulation, an 85mm layer of polyurethane foam can be sprayed onto the underside of the slates or tiles of a pitched roof. This stabilises and weatherproofs the roof by fixing the nails, battens and roofing felt. As the foam is a superior insulant, coupled with just 100mm of insulation at joist level, your roof will also meet the stringent thermal performance standards required for a new home. A typical roof can be insulated using the polyurethane treatment for around half the cost of re-roofing.
Polyurethane Spray Foam Insulation is used in industries ranging from mining to movies, from cold storage to marine flotation. Spray Foam Insulation’s ability to seal out air and insulate quickly means it’s always in high demand for residential and commercial applications. Spray Foam Insulation is critical for solving our nation’s energy challenges because it dramatically reduces the energy needed to heat and cool our homes and offices. https://youtube.com/watch?feature=youtube_gdata&v=ggLAUsiuI_o
Yes, a new roof should be coated if the building owner wants to add a highly reflective roof coating to reduce energy costs. The buyer should be aware of any warranties provided for a new roof that may violate that warranty during the period it is in force via the use of a roof coating. This will extend the roof’s service life. A reflective roof coating will reduce the heat load on the roofing assembly.

Yes, you're right that all of the problems mentioned above are related to the installer. I didn't try to hide that and even used the word 'installer' in two of the four headings. I can see how you'd think that the title is misleading, but in the end you can't separate spray foam insulation from its installation. Some people have the mistaken impression that if you get spray foam in your house, your home will outperform all others. My point here is that that's not true. https://www.youtube.com/watch?v=ggLAUsiuI_o&feature=share
We have a 22 year old home located in southeastern georgia where the humidity is very high. In the past 2 weeks our floors have started buckling all over. We have a vented crawl space and the old insulation is drooping from moisture and the wood is wet. We are debating between the "encapulation" method or the spray foam method to repair this issue. Which would you recommend?
Closed-cell (aka two-pound foam) is denser than open-cell at about 2 pounds per cubic foot. Its R-Value is between 6-6.5 per inch. As a result, this kind of foam is much more expensive than its counterpart. The reason closed-cell doesn't need a vapor retarder is because it already has one. It's permeance is 0.8 perm, which means it can handle cold climates without the use of an additional board or drywall. Closed-cell uses hydroflurocarbons (HFCs) as part of its makeup. However, this material has been known to have a high global warming effect. If you want a green insulation solution, this is not the material to use. A way to avoid this and still use closed-cell is by installing it alongside fiberglass batts. http://www.youtube.com/embed/ggLAUsiuI_o
Spray foam insulation or spray polyurethane foam (SPF) is an alternative to traditional building insulation such as fiberglass. A two-component mixture composed of isocyanate and polyol resin comes together at the tip of a gun, and forms an expanding foam that is sprayed onto roof tiles, concrete slabs, into wall cavities, or through holes drilled in into a cavity of a finished wall.
Apply coating when the roof is dry and the sealant has set. You will be using a 9-inch heavy-duty frame, ½-inch paint roller for spreading coating on roof or 1-1/4-inch roller for dipping in pail, and a 5–to-6-foot extension pole. Use a 3/4-inch roller with basecoats and emulsions. Map out your roof and make each pail fill that area. See Elastek Product Sheets for recommended coverage. An inexpensive 3-inch or 4-inch brush should be used to reach areas not possible with a roller. Use a stiff paintbrush for applying 103 Crack & Joint Sealant.
If you haven’t considered spray foam insulation, now may be the time to start looking into it. As you know, having proper insulation will help reduce your heat and air conditioning bills. In specific, spray foam insulation can be particularly helpful during renovations. It can provide a barrier between outside walls, and even a sound barrier for the inside.
I don't know if it's common or uncommon, but installing a layer of rigid foam above your roof sheathing in order to interrupt thermal bridging is always a good idea, and is preferable in all respects to a roof assembly without any rigid foam above the sheathing. If you decide to install rigid foam above the roof sheathing, you shouldn't use closed-cell spray foam under the sheathing; either use open-cell spray foam (which is vapor-permeable) or a fluffy insulation like cellulose, mineral wool, or fiberglass (any of which will allow the roof sheathing to dry to the interior).
Low-density foam is applied as low or high-pressure, two-component polyurethane spray foam. Low-density spray foam can be applied on walls, in unvented attics, to ducts and ceilings, and in vented attics and crawl spaces. It is known as an air barrier, but permeable to vapor and moisture. It is often used to fill cavities in walls during construction.
Light-density open-cell SPF is commonly known as half-pound foam. It is a semi-rigid material with a sponge-like appearance that expands during installation and creates small, open cells that are filled with carbon dioxide. Due to its ability to expand during the application process, it fills cracks, crevices and voids and adheres to irregular surfaces or substrates to form an air sealing insulation.[12]
RetroFoam of Michigan has more than 15 years of experience insulating thousands of homes and pole barns across the lower peninsula. We hear a lot of misconceptions about foam insulation and work to make sure we clear up any wrong ideas about foam insulation. Our staff helped us put together this list of misconceptions adding their insights to dispel any misinformation.
Good article, but it seems like you can chalk up almost all of those problems to the experience level of whomever is spraying the foam. Spray foam isn't an inherently bad product, but it's pretty easy to botch if the hired company is inexperienced. Fiberglass may be foolproof to install, but then again it has a terrible R-Value compared to a good spray foam. People just need to get referrals and do their homework whenever they research a spray foam contractor.
In general, cantilevered steel beams are a nightmare. If part of the steel beam is in contact with exterior temperatures, then it's best if the interior portion of the steel beam is covered on all sides with insulation. This is generally impossible (because the interior portion of the cantilevered beam generally supports a load, meaning that you can't wrap the steel beam in insulation on all sides).
High-pressure systems can be used to spray all three types of spray polyurethane foam. Of the three types of spray foam used in building insulation and weatherization, the high-pressure, two-component spray foam is most likely to be used on larger projects such as a new building construction or renovations. SPF applied with a high-pressure system tends to adhere tightly to the entire structure which helps avoid sagging or detaching from its position. It can also provide a seal against air and insects.
Sean, thanks for jumping in and answering John's questions. About choosing the right foam, I intentionally avoided the open cell vs. closed cell foam debate. I did this partly because it's worthy of an article all by itself, but mainly I didn't include it because, despite all the warnings the two sides issue about the other, I've never personally seen a problem caused by using open cell where they should've used closed cell or vice versa. I'm sure things like that happen; I just haven't seen it yet.

Spray Foam Attic Insulation

×